When we change new power capacitor (PF Improvement)?
(OP)
When we change new power capacitor (PF Improvement)?
Ex. Cap 50 kVAR 400V Ir = 72.2 A Cab = 497.36 uF(Delta connection)
In catalogue shown -5% to +10% (Tolerance 472.5 - 547.1 uF)
- Why new cap have Capacitance more than calculated value?
Ex Ccal = 497.36 uF Cnew = 570 uF(more than 10%)
- When we change new power capacitor?
Cmeasured <= xx% of Ccal or Imeasured <= xx% of Ir
Ex. Cap 50 kVAR 400V Ir = 72.2 A Cab = 497.36 uF(Delta connection)
In catalogue shown -5% to +10% (Tolerance 472.5 - 547.1 uF)
- Why new cap have Capacitance more than calculated value?
Ex Ccal = 497.36 uF Cnew = 570 uF(more than 10%)
- When we change new power capacitor?
Cmeasured <= xx% of Ccal or Imeasured <= xx% of Ir






RE: When we change new power capacitor (PF Improvement)?
RE: When we change new power capacitor (PF Improvement)?
In Delta loop had Cx, Cy and Cz,
So when we measure at terminal AB, Cab = Cx // (Cy + Cz)
at 50 kVAR 400V Cab = 497.36 uF