X/R ratio of Generator

X/R ratio of Generator

X/R ratio of Generator

(OP)
Dear Folks,
I have started power system modelling very recently. For generator modelling, in X"/R -ratio, which resistance we have to consider? between phases or phase to neutral (for star winding generator)
I tried with both resistances for calculaing Transient and sub-transient fault currents  but not matching with Generator supplier's fault current data which is attached.
The generator manufacturer has given max. 3ph. Symm.S.C. current:8314A (Is it steady state fault current or Transient fault current).
Your reply will be highly appreciated.
and thanking you.

RE: X/R ratio of Generator

Are you conducting fault at the line terminals of your generators ?

RE: X/R ratio of Generator

(OP)
Thank you tin2779 for clarification regarding resistance. What is current given in decrement curve - Max. 3 ph. Symm. S.C. current. Is it sub-transient/transient or steady state fault current?
Advanced thanks..

RE: X/R ratio of Generator

8314 A I believe is a subtransient Sys. fault current within Td" period (Start from 0.01s-0.1s). ASys.value would be the peak value as mentioned in the drawing 1.732 X 8314 A half cycle after fault.
Don't know why the LN fault or LL fault current increases after fault ? - Lack of damping?

RE: X/R ratio of Generator

(OP)
Thank you QBplanner,
Fault current should be reduced generally from sub-transient state to Steady state.
But in the attached decrement curves, as you said, L-L & L-G currents started increasing.
What are the possibilities?

RE: X/R ratio of Generator

Hi power2020:
A typical curve should be like the one I attached.
Don't know how and what they did to get the curve you may want to go back ask them the detailed modeling of both machine, exciter and fault.
Regards,

RE: X/R ratio of Generator

(OP)
Thank you QBplanner,
I will ask manufacturer, the reason for increasing trend of L-L and L-G fault over a period of time.
W.r.t. typical attached curve, what is the reason for increasing fault current after approx.0.1 sec.

RE: X/R ratio of Generator

Could the increase be from voltage regulator action increasing the field current in response to the fault? 100mSec seems a little quick for a voltage regulator response when the time constants of the field windings and exciter windings are considered.

RE: X/R ratio of Generator

I would believe it is because of the AVR.The fast of AVR can be acted  within 0.1 Sec.
Regards,

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources