Motor winch voltage problem
Motor winch voltage problem
(OP)
Hi guys,
I was wondering could you guys help with the following problem.
The problem is this, I have a client who is looking a 415v motor winch installed on a ship.
The winch is mobile, and is used on and off shore,
One big problem is that the supply voltage on the ship, is 230v three phase.
Considering the motor only works on 415v, what is the best way to solve the problem.
I have considered a transformer, but the current for this winch is 20A per phase AT 415v full load, and a starting current of 63A.
A transformer at 230v three phase will pull to much current into the primary taps, as the ship only offers a 32A supply.
HELP!!!!!!!!!
I was wondering could you guys help with the following problem.
The problem is this, I have a client who is looking a 415v motor winch installed on a ship.
The winch is mobile, and is used on and off shore,
One big problem is that the supply voltage on the ship, is 230v three phase.
Considering the motor only works on 415v, what is the best way to solve the problem.
I have considered a transformer, but the current for this winch is 20A per phase AT 415v full load, and a starting current of 63A.
A transformer at 230v three phase will pull to much current into the primary taps, as the ship only offers a 32A supply.
HELP!!!!!!!!!





RE: Motor winch voltage problem
RE: Motor winch voltage problem
230V*32A = 7360W existing
415V*20A = 8300W desired for just this motor
You are 1000 Watts shy and this is with everything else on the ship turned off. I would look into either upgrading the existing system or adding some additional generating capacity.
RE: Motor winch voltage problem
Just though you guys might know a way around this.
I will look at the winch motor, and see if i can get a smaller one to do the job.
Thanks again for the replies much apprieciated.
RE: Motor winch voltage problem