Current 180 degrees out of phase with Voltage

Current 180 degrees out of phase with Voltage

Current 180 degrees out of phase with Voltage

(OP)
Gents,

Little help please.  Currently investgiating some intermittant faults on a server room distribution board.  At the moment the UPS systems kick in and out randomly as a result of suspected voltage fluctuations.

To check our supply we monitored the supply to the board with a power quality meter and found from looking at the phasor diagram the whilst blue and yellow pahse had current slightly leading voltage blue phase was 180 degrees out of pahse with the voltage.

We suspect it may be due to a neutral fault but would like some back up.  

Has anyone come accross this or from theory suppose what is the problem other then a neutral fault?   

RE: Current 180 degrees out of phase with Voltage

Was the current sensor installed on that wire backwards?

RE: Current 180 degrees out of phase with Voltage

(OP)
Already checked that.  Rookie mistake.  Nope.

RE: Current 180 degrees out of phase with Voltage

The only thing I can add is that one of my rules of thumb is the following:

When everything looks crazy, start checking the continuity of the return lines.

RE: Current 180 degrees out of phase with Voltage

As I understand your information, look for an inverter with the leads swapped. As I understand the information, it sounds like a transformer in a 3 phase bank with X1 and X2 swapped.
respectfully

RE: Current 180 degrees out of phase with Voltage

What is the operating voltage 120/240 or 120/208 is this a single phase or three phase system or a European voltage system.

RE: Current 180 degrees out of phase with Voltage

(OP)
Guys found the problem.  Apparently the electrician DID have the sensor backwards.  Most embarrasing but it does happen....

Apologies to all.

RE: Current 180 degrees out of phase with Voltage

Ever so modestly...wiggle

RE: Current 180 degrees out of phase with Voltage

Your hint should have been when you noticed that the other two legs had leading (not lagging) power factor and the third as you said was 180 degrees out of phase.  You know that you are measuring it wrong.  

Don't feel bad, I get about 10% of my measurements hooked up backwards the first time even though I try to be careful.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources