Dear Folks,
How to choose short-time withstand current and duration for MV and LV switchgear and also pl. specify IEC/IEEE standard.
Advanced thanks..
How to choose short-time withstand current and duration for MV and LV switchgear and also pl. specify IEC/IEEE standard.
Advanced thanks..






RE: Switchgear short time with-stand current
In ANSI world, you don't get many options for duration. Just need to make sure the 1/2 cycle and 5 cycle fault currents are less than the published ratings for the breakers you select.
The trick is in how the fault current is calculated. It is not a simple Ohms law calculation for ANSI-rated breakers. Guidelines are in ANSI C37.
You can find applicable standards and the standard ratings on GE, Cutler-Hammer or Square D websites.
RE: Switchgear short time with-stand current
I have read in one of the academic books that short-time withstand current duration shall be 1-sec if fault current / rated current is more than 40 and
3-sec if fault current/rated current is less than 40.
But it is not given clearly that which fault current - 1/2 cycle or 1.5 -4 cycle. And also I could not find in any IEC/IEEE standards.
And I enquired one of the famous switchgear manufacturer regarding short-time with stand current(Icw), they said it will be derived from 1/2 cycle and 5-cycle fault currents (from symm rms and Asymm peak currents).
RE: Switchgear short time with-stand current
From practical standpoint, the main concerns are usually the 1/2 cycle and interrupting ratings.
RE: Switchgear short time with-stand current
from:
IEEE TRANSACTIONS ON INDUSTRY APPLICATIONS, VOL. 40, NO. 6, NOVEMBER/DECEMBER 2004, "Comparison of ANSI/IEEE and IEC Requirements for Low-Voltage Switchgear"
RE: Switchgear short time with-stand current
For HV switchgear :-
IEC 60694 ( AS2650 )Clause 4.5
Rated Short-Time Withstand Current ( Ik )
The rms value of the current which the switchgear and control gear can carry in the closed position during a specififed short-time under prescribed conditions of use and behaviour.
The rated short-time withstand current is equal to the rated short-circuit breaking current.
Duration 1 sec unless otherwise mentioned.
LV Switchgear :-
AS 3439.1 : 2002 Section 7.5
See Table 4 for the relationship between peak withstand current and short-time withstand current.
RE: Switchgear short time with-stand current
I have seen in many locations using 3-sec duration for short-time withstand current which is not mentioned in IEC 60694.
Mr.Mnewman- As I dont have AS standards, pl. attach table-4, in AS 3439.1:2002.
Advanced thanks...
RE: Switchgear short time with-stand current
1 sec and 3 sec are the most common duration times specifed for short-circuit withstand capability.
I do not know how to attach documents in Eng-Tips so I will reproduce Table 4 from the AS 3439.1 :2002 for LV switchgear
rms value of short-circuit current = Ik
powerfactor = pf
n = ratio of 'peak short-circuit current' to 'short-time withstand current'
Ik => 5kA, pf = 0.7, n = 1.5
5 < Ik =< 10kA pf = 0.5, n = 1.7
10 < Ik =< 20kA pf = 0.3, n = 2.0
20 < Ik =< 50kA pf = 0.25, n = 2.1
50 < Ik pf = 0.2, n = 2.2
'Peak short-circuit current' is the peak (crest) of the current waveform half a cycle after fault inception.
Ik = i peak / ( sqrt(2) * ( 1.02 + 0.09 *e^-3R/X ) )
Note for HV switchgear the peak to short-time withstand current ratio is 2.5
If someone can tell me how to attach documents I can send more information.
RE: Switchgear short time with-stand current
The actual calculated prospective ( duty ) values must not exceed these values.
RE: Switchgear short time with-stand current
Thanks alot for your info.
It is clear to calculate short-circuit with-stand current. How do we decide duration of short-circuit withstand time?
Regarding attachment: We type our information in Step-1 message, similarly there is step 3 for attachments. After clicking "..or upload your file to ENGINEERING.Com", separate window will open. Again select browse for required location of the file and then select upload file.
File will be uploaded along with your information.
RE: Switchgear short time with-stand current
Short-circuit clearing times are generally less than one second.
Thanks for instructions on attaching files.
RE: Switchgear short time with-stand current
Many thanks for your great response.