Concrete Between Steel Beams

Concrete Between Steel Beams

Concrete Between Steel Beams

(OP)
I am investigating a 1-story structure that has 3 bays with (3) W12x22 beams runing 250" long 6'O.C..  12" thick concrete is located BETWEEN the beams.  When I analyze the steel, it is insufficient to support the concrete as a dead load + live loads and I believe that the concrete is actually working as a beam (self sufficient) in the long direction.

Can anybody offer any advice as to how I would make this determination?  I am trying to show that additional dead load could be hung from the underside of the steel beams but it is not possible if the beams are supporting the dead load of the concrete placed between them.

THANK YOU for any help that could be provided...

RE: Concrete Between Steel Beams

If the concrete is reinforced, I think it would be much stiffer than the three beams, and therefore, would carry most of the load.  To be sure, check the ratio between the EI of the three steel beams and the EI of the two concrete slabs.  Then, make sure the beams and the concrete slabs can carry the load assigned to each.

DaveAtkins

RE: Concrete Between Steel Beams

Do you know which way the reinforcement spans in the concrete?  Do you know if the concrete was shored when it was poured?

RE: Concrete Between Steel Beams

(OP)
I am sorry but I don't know the direction of reinforcement.  Should I analyze this slab as an minimally reinforced 20.83'(250") slab?

Thanks again

RE: Concrete Between Steel Beams

I guess you could assume temperature and shrinkage steel in the long direction.  Is there support (like a continuous concrete or CMU wall with adequate footing) for each end of each concrete slab?

DaveAtkins

RE: Concrete Between Steel Beams

(OP)
There is a rubble foundation wall that the concrete and the beam sits on.

RE: Concrete Between Steel Beams

You mentioned that this is a one story structure.  At what level is this concrete and steel beam platform - a mezzanine?

Do you know anything about the local history of the building - what it was used for?  Any record or skinny of why this construction type was used?  Machinery support?

Any indication of burn marks / discoloration on the exposed side of the steel beams that might indicate rebar being welded to the beam?

Mike McCann
McCann Engineering

RE: Concrete Between Steel Beams

I'm having trouble picturing this.  Is the 12" slab flush with the top and bottom of the 12" beams?  How do you know the beams are W12x22?

RE: Concrete Between Steel Beams

That's what I assumed from the post is that the slab isflush with the top and bottom of the steel section.  

In that the side of the two outside beams can be observed and measured, I would have to assume the dimensions measured fit that of a 12X22.

Mike McCann
McCann Engineering

RE: Concrete Between Steel Beams

(OP)
Yes exactly.  The structure is a messanine.The concrete is flush with the top an bottom of the beam and can be observed (measured) at each end.

I guess the question boils down to are the 2 elements(concrete and steel) working alone or in composition to some extent.  Or that the steel is "doing all the work" which is what I am trying to prove is not the case.

Thanks all for your interest and response.

RE: Concrete Between Steel Beams

With no more information, I think you can invoke IBC Section 3403.2, and safely add 5% of the existing load without calculation.  Question is: 5% of what?  I would take the minimum of 5% of the beam capacity, and 5% of the existing dead load.  If your additional load exceeds that, then you need to find out how the slab is reinforced.

RE: Concrete Between Steel Beams

Unless you know that the slab forms were shored, I think you have to assume that the beams carry the full dead load of the concrete.  For additional loads, I think you could assume the concrete in compression contributes to the capacity of the system.

RE: Concrete Between Steel Beams

(OP)
When you say shored, what exactly are you referring to?  That is, I can presume they were formed from the underside and shored during concrete placement?  How else could they have been poured in place unless you mean something different.

RE: Concrete Between Steel Beams

would measuring the deflection in the beams provide any clue as to what the concrete is doing and how it was placed ?

RE: Concrete Between Steel Beams

VB1 - If the forms for the concrete were supported on the beams, and no temporary falsework was placed under the beams or forms during pouring and curing, the beams carry 100% of the concrete dead load.

RE: Concrete Between Steel Beams

Did you measure the floor deflection?

RE: Concrete Between Steel Beams

I should also add that if there was shoring, the concrete dead load would be carried by the steel and concrete compositely - depending on if the details can achieve strain compatibility.

RE: Concrete Between Steel Beams

(OP)
I did not realize that about shoring the concrete as opposed to using the bottom flanges as supports for the forms.  Thank you.

No deflection measurements were taken.  I guess I could work backward if I measured deflection and determine how much load can be applied to the steel beam.

RE: Concrete Between Steel Beams


I think the deflection would only tell if the structure acts compositely for live load.

RE: Concrete Between Steel Beams

If the steel beam deflection under self weight of the floor only was say 3/4 inch (which I doubt it was designed this way), I would say the beam is carrying the slab self weight. Even if the live load is shared between the slab and beam, the additional live load deflection may overstress beam and cause a plastic hinge at midspan if the beam is actually carrying the slab weight. Do you have any pictures of the mezzanine?

RE: Concrete Between Steel Beams

Why not jack the three beams and measure response to a knowmn load? that way the actual beam stiffness could be determined to decide the capacity of the components. Measurement of existing deflections do not help unless you know the actual pre pour camber.

RE: Concrete Between Steel Beams

DRCI:

This is probably an obvious observation to all, but I thought I'd better mention it anyway...  

If you do jack the beam, I would suggest jacking, or loading the beam in the upward direction, not down.  The beam Will have more capacity in this direction, and be less likely to be distressed by the test.  

Mike McCann
McCann Engineering

RE: Concrete Between Steel Beams

DRC

I thought about that after I posted, and even if it were cambered for the slab weight and settled down to horizontal currently, then the ultimate strength of the floor is the same but the total deflection would be different. I think he needs to find out if there is any reinforcing in the concrete and look into the strains of the system to make a decision on capacity. Shored or unshored, I think you have the same ultimate capacity if the strains permit.

Serviceability issues need a look into current deflection.

RE: Concrete Between Steel Beams

Regarding slab jacking, I was thinking about this and the shored/unshored question I believe would make the determination of capacity from jacking the floor upwards unclear. The reason I say it is unclear is that if the slab has reinforcing it will be in the bottom of the slab, so the upwards response of the originally unshored floor would be different than the downwards response going past the self weight deflected position.

I also am not sure how I feel about forcing new deflection in the downwards direction without first knowing more about what is going on.

RE: Concrete Between Steel Beams

Ok, I may be just a little bored out of my mind and as the son of an aerospace engineer, I'm wondering if I should change directions.  I just a bit of a geek ... maybe a lot of a geek ... a Realtor after 20 years working in the medical and pharmaceutical sciences (BS Biology, UC Irvine) and MBA (East TN State U).  Any suggestions?  Is it worth the time (I'm just 50).

RE: Concrete Between Steel Beams

On the average, it would take you a minimum of four years in school, four years experience before you could take your PE (Civil), and another one or two years before you could qualify to take the Structural test - 9 to ten years.  

How long have you planned to live past 59?  Then again, if you are bored and single, maybe the college life...  Let's not go there.

Mike McCann
McCann Engineering

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources