what does 60/80/110 MVA TR. stands for?

what does 60/80/110 MVA TR. stands for?

what does 60/80/110 MVA TR. stands for?

(OP)
Can any body explain what does it mean 60/80/110 MVA?  for step up Power Transformers (60/80/110 MVA) 115/34.5kv,

regards

RE: what does 60/80/110 MVA TR. stands for?

Must be ratings with different means of cooling... minimum with ONAN, middle with ONAF, & highest with OFAF.
ONAN - Oil Natural Air Natural
ONAF - Oil Natural Air Forced
OFAF - Oil Forced Air Forced

Anand Sekhar

RE: what does 60/80/110 MVA TR. stands for?

Most of the transformer i saw was ONAN/ONAF/ONAF

The second ONAF come with a second stage of fan on the transformer so it can deliver more power since it's cool down by 2 stage of fan

RE: what does 60/80/110 MVA TR. stands for?

In ANSI land, you may also see it designated OA/FA/FA or OA/FA/FOA

RE: what does 60/80/110 MVA TR. stands for?

(OP)
Thanks every body, the cooling system was ONAN/ONAF/ONAF, and what confused me is that (the cooling system for the 80 &100 MVA is still the same using(ONAF), so how can the capacity of the transformer increases from 80 MVA to 110 MVA with the same cooling system, however what asekhar said makes sense as we can increase the capacity of TR by changing to OFAF

Any further remarks please

RE: what does 60/80/110 MVA TR. stands for?

raynh

tem1234 has already responded on your query.. the second stage ONAF switches on more fans to provide still higher cooling.

Anand Sekhar

RE: what does 60/80/110 MVA TR. stands for?

You may also have different ratings with the same cooling method by allowing a high temperature rise. Example, 80MVA with a 55C rise, ??? MVA with a 65C rise.

RE: what does 60/80/110 MVA TR. stands for?

Hi Jghrits,

Even thought still is common in the US to call the trasformer cooling designation as OA/FA/FA, the ANSI standard was revised a few years ago to make them more consistent with IEC designation. So the IEEE Std C57.12.00-2000 replaced the cooling designation OA/FA/FA by ONAN/ONAF/ONAF.


RE: what does 60/80/110 MVA TR. stands for?

Some transformers have two stages of cooling fans.  Middle rating is for one stage of fans running, highest rating is for both stages running.  This is only possible for larger transformers with large surface area in the radiators.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources