5 MVA Generator
5 MVA Generator
(OP)
Customer has a 5MVA Generator operating in island mode, and the question is what would be the biggest motor we could connect to this GEN considering a typical IEC 6Kv motor with starting current ratio of 6.5 times flc.Efficiency 95% and power factor 0.90, and a starting voltage of 80%





RE: 5 MVA Generator
What is the base load?
What is the generator AVR droop characteristic?
Since you mention 650% starting current, I assume that you are only considering DOL start, if you use other means of starting, you will be able to start higher rated motors also.
Anand Sekhar
RE: 5 MVA Generator
The FAQ237-766: Generator Sizing for a Motor Load Could help.
Regards
Petronila
RE: 5 MVA Generator
respectfully
RE: 5 MVA Generator
This formula could help: Motor HP x(KVA/HP) x (1000/Motor voltage)= LRA.
Taking account the Generator most be cappable to deliver all LRA Then the Gen Amps = LRA.
LRA= 5000 KVA /1.73 x (0.8 x 6) KV = 601 Amps. Is/Im = 6.5 then Im = 601/6.5 = 92 Amps where Is = Istarting= LRA and
Im= I motor.
Motor KW = 1.73 x Vm x Im x PF x Eff = 871 KW
If you have a generator capable to whistand a instantaneus over load of 300 % then the new Gen KVA= 15000 and the new LRA = 1803 the new Im = 277 Amps and the new Motor KW = 2465.
You most take account the Gen Set characteristics in order to know if is possible a 300% overload and it`s lasting time.
Regards
Petronila
RE: 5 MVA Generator
From what I've seen, most generators can support around 200% current for something like 10 seconds. So, for a full voltage start, Waross pretty much has it. Generator MVA x 2 / 6 or generator MVA divided by 3 meaning the motor could be about 1600kW. For reduced voltage start you can start a motor up to around MVA / 2 so the motor could be around 2500kW.
With a VFD you could get maybe get up to around a 4000kW motor or so. You have to take the efficiency of the motor and the VFD off the generator capacity. The motor and VFD together might be around 80% to 85% efficient.
Of course, this is all theoretical and it really depends on the complete system so it needs to be studied in detail.
RE: 5 MVA Generator
Keith Cress