MODELING A SINGLE-LINE TO GROUND FAULT

MODELING A SINGLE-LINE TO GROUND FAULT

MODELING A SINGLE-LINE TO GROUND FAULT

(OP)
Can anybody help me on a specific problem?

I tried short-circuit simulation on an MV ungrounded system and I can't seem to arrive at good results on a SLG condition. How do you model an SLG?

Any comment/ tip is accepted

RE: MODELING A SINGLE-LINE TO GROUND FAULT

What did you get and what are you expecting?

RE: MODELING A SINGLE-LINE TO GROUND FAULT

Hint:  Draw a circuit diagram showing the current path for a line-to-ground fault on an ungrounded system.  

RE: MODELING A SINGLE-LINE TO GROUND FAULT

You don't have fault current because the system is ungrounded.

Put a ground reference in your model whit moderate impedance to see some fault currents and voltages.

For example try including a reactor in your model whit very hig impedance.

Excuse my bad english.



RE: MODELING A SINGLE-LINE TO GROUND FAULT

Ungrounded system will not have earth fault current.

Anand Sekhar

RE: MODELING A SINGLE-LINE TO GROUND FAULT

Hi Anand.
It's not exectly.
Earth fault current in ungrounded(isolated)systems are depend on the capacitance of the system. ( lenght of cables, number of cabels, voltages, etc.)
Possible current up to few amp's, I see also about ten amp's.

You can continue work with this fault.
Best Regards.
Slava

RE: MODELING A SINGLE-LINE TO GROUND FAULT

Hi Slava,

I know that system capacitive currents exist & will depend on the size of the system & lenght of its cable network.  The capacitive contibution is calculated & used for setting of earth fault protection alarm / directional earth fault protection trip for unearthed systems. But I am not sure whether the capacitive contribution is considered as fault current in fault calculations / modelling. That is what I meant.

Anand Sekhar

RE: MODELING A SINGLE-LINE TO GROUND FAULT

Hi Anand.
Yes, we talk about same.
I agree with you 100%.
Best Regards.
Slava

RE: MODELING A SINGLE-LINE TO GROUND FAULT

(OP)
Thanks for the tips.

I tried inserting a single-phase load at the source generator. The load was set capacitive (I played around with values), but when I simulated an SLG fault on any bus, only the phase to ground voltages on rose to 1.73 times! I can't see the expected single-line to ground current!

RE: MODELING A SINGLE-LINE TO GROUND FAULT

You have to have ground path in your model.  The model doesn't know about the capacitive coupling to ground.  

It may not be possible to model it using whatever software you are using.  

As painful as it might be to consider, it may be necessary to calculate it manually - and you might actually learn something in the process.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources