Radiant Heat on SOG

Radiant Heat on SOG

Radiant Heat on SOG

(OP)
We have an 11-12 thick SOG for an Airplane Hangar (main gear loads 80k to 90k). The owner would like to install radiant heating. According to the HVAC salesman the tubes will be about 3/4" and they will be resting on the reinforcement. Even though they try to avoid crosiing any joints they cannot avoid all of the them. The bottom of the slab will be insulated for obvious reasons.   

Does anyone see any potential problems with this type of installation?

Thank you      

RE: Radiant Heat on SOG

Obviously at the construction joints.  

Could he provide a small covered junction box at the places where the tubing crosses the joints?  The box could be encased in the slab , and the line within the box could be flex line allowing for expansion/contraction w/o leakage.

Hopefully you have several separate runs of the 3/4" piping.  

Mike McCann
McCann Engineering

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources