permisible load on transf accor. to codes
Can any body please tell me what is the permissible load that can be connected to a power transformer (250KVA)for an ambient temp. which does not exceed 45deg. cen, indoor type according to the codes, the transformer is new .
RE: permisible load on transf accor. to codes
Oil insulated or dry?
40C is the standard rating for dry type. If the temp exceeds the rating, you should consult the manufacturer for applicable de-rating.
For steady state of load 80% may be suitable [ if you don't expect any future development].
For a short time [hours] the transformer could be overloaded without any damage [how much depend on manufacturer indications].
But you have to check if when starting the most powerful motor the voltage drop through the transformer [ loaded 80% ] is not too high so the voltage at the
other still consumer terminals does not fall under the permissible .
A thumb rule is the transformer KVA > 3*maxMOTOR KW
Thank you for yr reply, and I fully agree with you, however my load is lighting and HVAC and no further extension expected in the building, the 80% you mentioned , is it according to any international code? or it is subjected to the designer estimate?
Kind Regards
I don't know any code stating this. It is only my experience. In my opinion even 90% load is not so bad. But a slight reserve of 20% is better, I think. Nobody knows when a sudden extension -HVAC may be- will occur.