The client want us to design a 50% redundant HVAC system for them. In my opinion, 50% redundancy means we need 3 rooftop units with 50% capacity for each, anytime we just run 2 units to get 100% capacity and another one will be the backup, is that correct? Thanks.

RE: Redundant system

In engineering: serving as a duplicate for preventing failure of an entire system. That said I would Have one unit for 100% load and another as a stand by.

RE: Redundant system

(OP)
thanks all. two unit each with 100% load means 100% redundancy. now the question is about 50% redundancy.

RE: Redundant system

You need one AHU sized for 100% of the load and another backup size for 50% of the load.  That is the 50% redundancy.  Sometimes owners want this because they don't want to pay for two 100% units, so they feel that if something should go wrong with the main unit that they can get by on 50% temporarily until the broken one is fixed.  

RE: Redundant system

I just had a similar discussion with a client the other day andhe statement can be somewhat ambiguous and needs to be confirmed with the client.  Their reasoning was:

- 100% redundancy means if anything fails 100% capacity is available, ie two units at 100% capacity, 3 units at 50% capacity, 4 units at 33% capacity etc

- 50% redundancy means if anything fails min 50% capacity is available, ie two units at 50% capacity are required (or 3 at 33% etc)

For this particular project the requirement was 75% redundancy so four units at 25% full load are being installed, if any one fail 75% capacity is available which is still sufficient for most of the time.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources