sample cooler design

sample cooler design

sample cooler design

(OP)

I am new designer.
I am designing a sample cooler for Condensate sample. The Tie points for sampling station are discharge and suction of Condensate pump. The condensate is at 90 C and to be cooled upto 25 C. The line run will be around 20 feet (Tieing from discharge Pressure gauge to Suction drain valve of the pump).

Since Pressure drop is very high(800 Kpa) and line length is not much , the flow rate is huge ( through 1" line).

What is a good idea to control the flow of sample ? Use an orifice or a Globe valve ??

Utility water at 10 C/300 Kpa  is used for cooling. How can I calculate Utility water flowrate?


RE: sample cooler design

Pretty standard design.  You can probably find examples in your plant now if you go out and look.

Normal is block valves in and out of cooler on process and utility side.  Make sure your sample point is after the cooler and before the block valve.  Valve on sample point should be a needle valve to limit the flow of sampled material.

RE: sample cooler design

I do not recommend that you design your own.
Check out the following:
Graham Heliflow Heat Exchanger
Product Overview
The Graham Heliflow is a unique type of shell and tube heat exchanger. The tubes in the Heliflow are arranged in parallel, starting with an inlet manifold on one end, and terminating at an outlet manifold on the opposite end. The tube bundle is wound into a helical pattern. This coiled construction creates a spiral flow path for the fluid inside the coil.     Heliflow Heat Exchanger spiral flow path
Heliflow Heat Exchanger parts     Each tube is in close contact with the tube above and below it. The coiled tube bundle is fit into a two piece casing. When the casing is tightened, it is designed to slightly compress the tubes. Because of the tight fit, the shellside fluid is forced to circulate in a spiral patten which is created by the open spaces between the coils.
http://www.graham-mfg.com/heliflow.html

RE: sample cooler design

my previous employer used almost exclusively
http://www.dopak.com/
with good results (including highly toxic/carcinogenic streams)

RE: sample cooler design

Quite new in heat exchangers thermal and mechanical design.
Please recomend software, books, templates, methodology and more....

Thank you

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources