Three Way mixing valves

Three Way mixing valves

Three Way mixing valves

(OP)
Is better to use a diverting valve or mixing valve at the AHU on a chilled water system?

RE: Three Way mixing valves

It depends on weather the system is a constant flow or a variable flow system.
Three-way valves by their nature bypass supply chilled water into the return line, causing chilled water return temperatures lower than design. This exacerbates low delta -T problem. Therefor you want to  use a minimum of three-way valves in variable flow system. Two-position bypass valves across supply and return lines, strategically situated and controlled properly is preferred to ensure minimum flow.

RE: Three Way mixing valves

(OP)
The system will be constant. Thanks btw

RE: Three Way mixing valves

As I understand it, functionally there is no difference whether you use the mixing valve or diverting valve; however, I have seen more often than not, the mixing valve in these three-way valve applications (where the valve is in the return piping vs. the supply side of the coil where it would be a diverting valve).  I was told that this is because a mixing valve is typically less expensive than a diverting valve.

RE: Three Way mixing valves

We specify diverting valves on our projects. They have given us better cooling coil temperature control than mixing.

RE: Three Way mixing valves

stevenw:  I'd like to hear more about how exactly 3-way diverting valves give better cooling coil temperature control.

To reiterate the predominance of 3-way maixing valves, it's the reason you see two-way valves traditionally placed on the return side of coils (where the mixing valve would go as opposed to the diverting valve).

Ifc09:  Don't forget, when using the 3-way mixing valve,  you need a balance valve in the bypass line which matches the pressure drop of the coil so that a fluid "short circuit" won't occur.    

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources