Is better to use a diverting valve or mixing valve at the AHU on a chilled water system?
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Three Way mixing valves
Three-way valves by their nature bypass supply chilled water into the return line, causing chilled water return temperatures lower than design. This exacerbates low delta -T problem. Therefor you want to use a minimum of three-way valves in variable flow system. Two-position bypass valves across supply and return lines, strategically situated and controlled properly is preferred to ensure minimum flow.
RE: Three Way mixing valves
RE: Three Way mixing valves
RE: Three Way mixing valves
RE: Three Way mixing valves
To reiterate the predominance of 3-way maixing valves, it's the reason you see two-way valves traditionally placed on the return side of coils (where the mixing valve would go as opposed to the diverting valve).
Ifc09: Don't forget, when using the 3-way mixing valve, you need a balance valve in the bypass line which matches the pressure drop of the coil so that a fluid "short circuit" won't occur.