GuardLogix & SmartGuard on DeviceNet

GuardLogix & SmartGuard on DeviceNet

GuardLogix & SmartGuard on DeviceNet

(OP)
Has anyone setup communications between a GuardLogix PLC and a SmartGuard Controller on a devicenet?

I setup the smartguard for COS with 2 bytes input and 1 byte output data(on the RSNetworx for DeviceNet).

I had to create "Generic Safety Module" on the IO config on the Logix 5000.

But for some reason it comes back with the same fault "(Code 16#000c)Service Request Error:Invalid Mode or State for service request ". This fault appears on the module created on the Logix 5000 IO config. Any ideas how to fix it??

Thanks
Sriram

RE: GuardLogix & SmartGuard on DeviceNet

I don't think you can make a safety connection between GuardLogix and SmartGuard.

When you set up the COS connection with 2 bytes input and 1 byte output, that was in the "Slave I/O" configuration tab for the SmartGuard configuration in RSNetworx, right ?

You can put that connection in the Scanlist of the 1756-DNB and map it into the normal I/O data table, but I don't think you can connect it as a Safety device in the RSLogix 5000 I/O tree.

RE: GuardLogix & SmartGuard on DeviceNet

(OP)
Yes U  are absolutely right about that. Contrary to what the user manual says, u cannot add the smartguard in the IO tree of the Logix 5000 software. U have 2 add tags in the "Slave I/O" configuration tab in SmartGuard configuration in RSNetworx so that it appears in the "scanlist" of the DNB scanner.

Also U cannot make safety connection between GuardLogix and SmartGuard. The "safety Slave I/O" tab is for connections between two smartguards on the same network ONLY.

Well another issue I had was in the "Logic" editor of the SmartGuard in RSNetworx where u can add function blocks, I found that there is no way to add temporary "base" tags. Every tag u use in the "logic" editor should be pre-defined in the "slave I/O" beforehand to be used. They call it the "name" tags. Is my understanding right?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources