Automax actuator and H-4000 positioner
Where can I find technical reference material for an Automax model R312PSR80 actuator?
It is being used here with a butterfly valve on a 24" line.  The positioner is an Automax H-4000 with 4-20 I/P and 3-15psi output.
Specifically, I need maintenance data to troubleshoot, test and prove the operation of the 90 degree span butterfly.  The actuator R312PSR80 has 2 air chambers.
I need specifics on the ports, connections and operation of this device.
Thanks in advance!
RE: Automax actuator and H-4000 positioner
PetroChef,
              Automax is a brand of FLOWSERVE Corporation, so you should browse into the site http://www.flowserve.com/eim/Products/HeritageBrands/Automax
              May I ask what type (and possibly model and/or manufacturer) of butterfly valve you are actuating?
Thanks,                'NGL
H4000 positioner is obsolete but it is calibrated much as any force-balance positioner.  Zero-adjustment is a thumbwheel at the bottom of the spring.  Span adjustment is at the top of the spring and changes the stiffness by changing the number of active coils,but that does interact with the zero setting.  Once the span adjustment is set it does not drift, and the only adjustment you should ever have to touch again should be the zero if you disturb the cam or move the positioner to a different valve.  Current replacement for the H4000 is the APEX type 5100 positioner, which has noninteractive zero and span.
To set the zero, apply 4 ma to the contacts and watch the output gage.  Apply very small movements to the zero screw until the valve begins to move.  Back off on the screw until the valve closes and the Output Pressure needle just falls to zero.  Best to make very small movements and wait to see what happens for 15-20 seconds. Once the unit is zeroed, apply 18 ma, then 19, then 20, and the valve should stroke to full travel at 20 ma.  Since the span and zero are interactive, if you find it necessary to set the span, you will need to reset the zero. You can chase yourself for hours unless you set the span first and then dial in the zero.
To set the span, first loosen the lock screw at the top of the spring so the spring can be rotated. At zero signal, adjust the span spring a tiny amount.  apply signal gently and record the signal at which the valve starts to move. Do not touch the zero adjustment. Keep increasing signal and record the signal at which the valve becomes fully open. When you have the span correctly set the difference should be 16 ma.  If you don't have a 16ma span, Tweak the adjustment and repeat the span measurement until you get 16ma.  THEN set the signal at 4 ma and adjust the zero adjustment until the output gage goes to zero.  Make small adjustments. You can overshoot and miss the correct zero setting easily especially with such a large actuator.  It takes a while to respond to tiny incremental changes.
Automax refer to the R312 as a "Heavy-Duty" actuator.  If you go to the flowserve.com  site,and select literature, automation, automax, and instructions, it will lead you here: http://www.flowserve.com/vgnfiles/Files/Literature/FCD/auto-9-e.pdf
Download the instruction bulletin for the actuator.
312SR80 does have 2 air chambers as you mention but since it is spring-opposed the inner one is not used. The pneumatic connection to the inner chamber ( the one nearest the scotch-yoke housing) should be vented with a screened vent.  If you leave the hole open you may get dirt-daubers.  If the vent hole is plugged the valve will not open fully.
Not picking on you but this is widely mis-specified.  The positioner does NOT have a 3-15 psi output.  The output of any positioner you'd care to measure is from zero to full supply pressure.  The 80  in the model code 312SR80 means that the actuator is supplied with a spring-pack optimized for 80 psi supply.  Feed it 3-15 and it will never even lift off the stop.
Thanks for the replies; I did finally get a start on it by finding similar actuators on the web, and surmising the operation.  As I said, I had NO information to start with.
Turns out to be a Scotch Yoke, Air-to-Spring, Heavy-Duty Actuator.
The Flowserve site did not help, mainly because I was not familiar with it.  They call it a "Heavy Duty" actuator, and treat it separately; a search on the model number yielded nothing.
Once I understood what we had I was able to get silicone oil into the chamber ane rejuvinate the rubber seal enough operate the valve to the open position.  This put us back in production, and I have requested Viton seals (0 to 300 deg F) in place of the standard nitrile which came in the unit originally.
After all that, I received the email replies, and am most grateful, especially for the site address for the device.
Too bad everyone here was crying "Positioner! Positioner!" which cost time and money.  If idiots could fly this would be an airport.
Thanks again for the assistance!
JRS
The Flowserve site did not help, mainly because I was not familiar with it.  They call it a "Heavy Duty" actuator, and treat it separately; a search on the model number yielded nothing.<<
um, I gave you a link directly to the IOM for the actuator in question........When I click on it the document opens, I was hoping it would also do thet for you.
Jim;
Thanks for your help; the link did, of course, lead to the spec sheets for this actuator.
JRS