round concrete column
round concrete column
(OP)
Is there a limitation on the spacing of the vertical reinforcing around the perimeter of a round concrete column. With round ties, is it to be limited to 6" per ACI 318? Or do round ties let me go further than 6"?






RE: round concrete column
RE: round concrete column
http://www.concrete.org/318QA/afmtopics.asp
RE: round concrete column
Aside from meeting the 1% min and 8% max steel area I don't think the vertical bar spacing matters for circular ties.
RE: round concrete column