I cannot find a code provision for a safety factor when resisting buoyancy. Can anyone point me in the right direction?
TIA
TIA
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Buoyancy Safety Factor
RE: Buoyancy Safety Factor
RE: Buoyancy Safety Factor
I'd say it depends on what you are designing. According to Design of Liquid Retaining Concrete Structures by R.D. Anchor, "The safety margin required is a matter of judgement of the designer. Dependent on the certainty with which the ground water level is known, the factor of safety may vary between 1.1 and 1.25." For environmental structures, we've always used 1.15.