I am trying to find some information about winding heaters. I need to know if it is worthwhile installing some on a generator at work. I would appreciate it if someone could please point me in the right direction.






RE: Heaters for standby generator windings
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: Heaters for standby generator windings
RE: Heaters for standby generator windings
Site knowlege
Cost benefit.... What rating is the set? What does it support? An office or your hospital's operating theater?
Heaters cost say $500 (ask your supplier)
Is this a worthwhile investment at this specific site to ensure that mosture does not cause a problem and result in a flashover in the alternator?
RE: Heaters for standby generator windings
A common installation is half voltage on the heater for dependability and long life. The heaters are placed low in the alternator and often heat the stator by convection rather than direct conduction.
For condensation protection forget the thermostat. Use a heater rated at twice the available voltage and leave it on. Use a relay to cut off the relay when the generator is running.
Search this site for more information.
respectfully
RE: Heaters for standby generator windings
Usually you want to get the heater built into the generator to save the hassles.
Can you get a heater from the maker? Then you know it will fit easily.
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: Heaters for standby generator windings
I normally use the formula - space heater wattage = 13DL where D&L are the diameter and length of rotor in cm.
I use two single phase heaters (one on each side of the core and below the end winding) connected in series.
This produces a wattage= 1/4th of the total of the two heaters wattage.
e.g. 2 nos. 200 V, 200 W heaters connected in series and supplied with 200 V, will produce 100 watts.
Connecting two heaters in series will ensure
1. least heater failure (because of reduced voltage and current)
2. No red-hot operation of the heaters (due to less watts/surface area)