(OP)
I'm working on the expansion of an outdoor substation, and I'm looking for a practical guide to design the new earth grid. I have limited information on the existing one. Earth resistivity tests are beeing done now.

Any suggestion on such a practical guide??

It's a 25 kV sub, with 2 txfos (25kV/4kV  & 25kV/600V both resistance grounded), capacitor bank, breakers etc.., the actual fence will be moved about 20 feet out on each side.

Thank you

JL

RE: Practical guide for ground grid design

Hi JLuc
I think you have no problem to calculate the GROUNDING GRID FAULT CURRENT.
In order to build a Grounding Grid and calculate GPR and Touch and Step Potential this link may be useful:
http://www.erico.com/public/library/fep/LT0359.pdf
regards

RE: Practical guide for ground grid design

A classical guides are the IEEE Std 80 for the US and other ANSI market place and CENELEC / IEC Std 479-1 for European countries and other IEC market places.

RE: Practical guide for ground grid design

(OP)
thanks for the suggestions.

the IEEE Std 80 helped a lot. Good "step by step" design procedure.

JL

RE: Practical guide for ground grid design

The problem will be with the unknown existing grid.  For safety in the expansion area, you could assume a minimal grid in the existing substation.  If the expansion increases fault levels at the existing substation, however, you need to check to ensure that the existing substation is safe.  I see two choices.  First, locate the existing grid and ground rods.  Second, install new grid wires and/or ground rods in the existing substation area.  Neither option is easy, particularly in an energized substation.

The CDEGS 2003 Users' Group Conference included a paper on the Assessment of Earthing Systems at Existing Substations by Mark Davies and Matthew Taylor, Strategy & Solutions Ltd, UK.  You might get information on this at the SES website http://www.sestech.com/.  If not, you could contact SES to get a copy.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources