Steam condensate question

Steam condensate question

Steam condensate question

(OP)
If I have a LPS entering a coil, but I can not return by gravity. I have to pump the condensate pump back to the bfu, how do I calculate gpm.
Do I just find lbs/hr and then calculate using 1lb-water/hr = 8.34 gallons/lb-water x 60min/hr x SG
which gives me 1lb-water/hr = 500 gpm

or do I calculate gpm by:
btu/h = gpm x 500 x Tdiff
with btu/h = 960 x lbs/hr

RE: Steam condensate question

You're multiplying instead of dividing.

GPM Cond = (#/hr steam)/(8.35 #/gal)/(60min/hr)

So 1#/hr equals only 0.002 GPM

Since you have LP steam, flash loss in the condensate pump won't be enough to affect the GPM selection.  If you know your steam load, you can calculate GPM.

RE: Steam condensate question

BronYrAur, Don't you have to find lbs of water first?

RE: Steam condensate question

500 lbs of steam per hour will give you 1 USGPM of condensate to pump or dump.

8.33 lbs of water per US gallon, times 60 minutes per hour = 499.8. Round it to 500 lbs/hr.


Check out the publication "Hook-Ups" by Spirax-Sarco. It's full of info like this. If you're threatening to buy some of their products (traps, control valves, condensate pumps, etc.) the local rep will likely give you a copy or two.

RE: Steam condensate question

TBP
Close enough however it will vary as the pressure goes up and down.

RE: Steam condensate question

imok2 - Nope, it's constant. 1 lb of water will evaporate into 1 lb of steam, which will condense back into 1 lb of water. The latent heat will vary, but that's another story.

RE: Steam condensate question

Yes I was referring to the latent heat of vaporization which would increase as the pressure would increase hereby increasing the condensation and visa versa.

RE: Steam condensate question

One thing to remember is the warm-up load.  I would suggest a 2:1 safety factor, although I have seen it as high as 2.5:1.  It all depends on how fast you are warming up.  

So for each 1 Lb/Hr of rated load, figure 2 or 2.5 lb/hr required for warm-up.  You condensate pump will have to handle this additional load and must be sized accordingly.  So your max pump load will then be 0.004 or 0.005 GMP for each lb/hr of running steam load.    

RE: Steam condensate question

But isn't that why you have a condensate tank? Anyone involved with this kind of work really should check out "Hook-Ups". It is an awesome publication, and the local rep will usually give you one.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources