Increase in soil height with a cast in place basement wall
I have searched the posts and have not seemed to find one similar to this so I will give it a shot. I have a client working on an existing hospital in SC. The hospital is being renovated and the existing grade adjacent to the basement walls needs to be raised approximately 5 feet. I am currently trying to figure out the increase in pressure along the face of the wall and what my options are for raising the grade. Removing the wall is not an option and reinforcing the wall further may not be either. Ineed to come up with a solution for raising the grade without increases the pressure on the wall. No design/specifics are available as to the construction of the basement wall. I figure if I do not increase the current condition then we would be safe.
The basement wall is 16 tall and backfilled with 11' of soil. I do not know the specifics on the soil type. I am assuming a combination of a clayey silt, silty clay being that those are the majority of the soils located here. The grade needs to be raised 5' in around this basement.
Doing some preliminary calculations I have used the at rest condition and solved the pressure per foot along the wall with Po=.5[ko(gamma ')H]H. Is my assumption right the wall is at an at rest condition. My calculations came to 3,620 #/ft for the existing condition with 11' of soil backfill.
Scenario 1: Raise the wall with soil assuming gamma' is 120 pcf. Po=7,680#/ft (No good)
Scenario 2: Remove the 11' of backfill soil and replace with 16' of 57 stone. Po=7,040. (No good)
Scenario 3: Remove 11' of backfill and replace with 16' of lightweight aggregate (SOLITE)
Po=4,800#/ft (No good)
Foam was also brought up but the cost seems way too high.
Any suggestions/alternatives would be greatly appreciated. I have not been on here long, but I really enjoy reading the posts and replys. Very imformative.
RE: Increase in soil height with a cast in place basement wall
Do you have any existing drawings on the wall and its foundation?
Mike McCann
McCann Engineering
Jason Vaughn
smeinc.com
Mike McCann
McCann Engineering
See link for example:
ht
Alternatively you could consider driving permanent sheet piles adjacent to the existing wall prior to filling but this may be expensive and there may be vibration issues depending on what equipment the hospital has installed in the basement.
Hope this helps.
Your link is not a bad idea if it is not too close to the property line. Skeptical about the sheet pile though.
Mike McCann
McCann Engineering
You could also remove the soil and replace it using a mechanically-stabilized embankment with a wrapped face against the existing basement wall. This could essentially remove the earth pressure from the basement wall.
Just a few ideas to add to what's already been offerred. . . . . .
f-d
¡papá gordo ain’t no madre flaca!
The SE chose to trench and install a concrete wall that pinned between the footing and the 1st floor diaphragm. probably a more expensive option then you're looking for. you could also trench in a gravity wall if you can't pin it.
if you go with any washed stone options, make sure your drainage is done well.
The potential change in soil load path is the X-factor. Old buildings don't like new tricks and soils never went to college.
is SME branching out, or is this part of a prelim geotech report.
I really like the idea of placing the mechanically-stabilized embankment with a wrapped face against the existing basement wall. Thanks fatdad.
Thanks to all for your replies.
be careful about the wrapped faces - they are really hard to build and if the contractor messes up you are totally up the creek. Ese a steel mesh face and for God's sake use good backfill!
be careful about the wrapped faces - they are really hard to build and if the contractor messes up you are totally up the creek. Use a steel mesh face and for God's sake use good backfill!
I'm still thinking solite would work. . . . .
f-d