partial discharge between coils exiting same slot (13.2kv)

partial discharge between coils exiting same slot (13.2kv)

partial discharge between coils exiting same slot (13.2kv)

(OP)
Machine Data: 13.2kv 8000 hp, vertical induction motor
70C rise, 307 A FLA 1182 rpm, Class F epoxy VPI Insulation,
Stress control treatments: The semicon is tape and the grading is paint.

108 stator slots
Coil Span = 1 to 14 slots, 3-circuit wye connection, 12 coils in series per leg,
11 turn coil, 2 wire wide.
6 - slots per pole per phase.

Approximately 20 years in service. In-plant periodic megger and dc step voltage tests have been satisfactory. P.D. results have been stable since pd monitoring installed in 2001. A and B phases are approx 100 mv +/-. C is approx 250 (QM+) and 150 (QM-). (We are looking at the pd data a little closer.)

Motor was removed for it's first-ever routine time-based refurbishment/inspection. During inspection, it was noted:

1 - There was a single visual indication of partial discharge (whiate powder) at location of an RTD lead (slide 1).

2 - There is a recurring pattern of partial discharge (white powder) around the stator in groups of 2-3 slots separated by 12 slots. In all cases the partial discharges is located in between coils sharing the same slot at a distance of 1"-3" above the slot on the top end of the motor (connection end). No similar pattern on the bottom end.

We are looking to map out exactly where these coils fit into the circuit and to inspect the clearances a little closer.

Any comments on the severity of this condition? What further inspection or testing would you suggest to evaluate? Do you think it can be repaired or will require a rewind? (this is a critical motor application)

http://home.comcast.net/~electricpete/eng-tips/Presentation.ppt

=====================================
Eng-tips forums: The best place on the web for engineering discussions.

RE: partial discharge between coils exiting same slot (13.2kv)

Thanks Pete for share with us your experience.

Petronila

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources