neutral protection from residual connection OR zigzag ct

neutral protection from residual connection OR zigzag ct

neutral protection from residual connection OR zigzag ct

(OP)
we have a new installation: a 25 kV feeder from a Y-D txfo, with a zigzag txfo. what is the common practice to protect that feeder from phase/ground faults. should I use residual CT connection from the overcurrent protection, or sould I use a CT from the neutral point of the zigzag. the overcurrent protection and the neutral overcurrent protection are done on the same relay -> multilin MIF II.

thanks

JL

RE: neutral protection from residual connection OR zigzag ct

Normally, I'd use both, if possible.  And I'd consider a backup relay if this is a major feeder.  

RE: neutral protection from residual connection OR zigzag ct

Phase CTs located between the two transformers won't seen the ground fault current.  You would need to locate the phase CTs beyond the grounding transformer or use a CT in the neutral.  Either works, which is best depends on the particulars of the installation.

RE: neutral protection from residual connection OR zigzag ct

Assuming the Zigzag trafo is connected at the transformer secondary terminals (before the incomer breaker at the switchboard), both phase CTs located in the switchboard incomer panel as well as the neutral CT in Z-trafo should see the earth faults downstream.
Thus, you will be able to use either or both of the methods (residual current or neutral CT)for earth fault protection.
As dpc mentioned, it is better if you could have two earth fault protection elements, one connected to the residual input and the other neutral CT input.
However, checkout the relay manual, many relays don't have provision for accepting two inputs.
In such a case, the neutral CT input becomes obvious choice. The residual connection always leaves a possibility of spurious earth fault protection operation, due to differences in the phase CT characteristics.

RE: neutral protection from residual connection OR zigzag ct

Small aditional remark.
You can use MIFII with residual connection for ground fault protection. MIFII are include only one CT input for 51N function.
CT on neutral side of zigzag xfr. is possible connect to transformer protection.
Of course you need provide some coordination between these functions.
Regards.
Slava

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources