Can you ommit a shear wall holddown?

Can you ommit a shear wall holddown?

Can you ommit a shear wall holddown?

(OP)
If you have a wood shear wall and it's long enough, can you use the sill plate anchorage to replace the typical end-of-wall shearwall holddown?  Theres no code requirement for holddowns and I think its more of an analysis decision.

Never seen it done, but am looking at a set that has this.

RE: Can you ommit a shear wall holddown?

Its all in the load path.  If you can transfer the tension force in the stud(s) to the sill plate, if sill plate can transfer the load to the anchor bolt, and if the anchor can transfer load into foundation, then I say it's good. You might want to make sure the remaining anchors can take the shear/direct uplift load without the one you are using for a hold-down.

j

RE: Can you ommit a shear wall holddown?

Also, if there is sufficient dead load on the wall to resist the overturning moment, a hold-down is not required.

RE: Can you ommit a shear wall holddown?

Also, in a special case where a transfer beam is over the top of the shearwall, the holddowns can be omitted on the shearwall, but, depending on the dead load afailable to resist overturning, may have to be applied to the transfer beam and associated column connections.

Mike McCann
McCann Engineering

RE: Can you ommit a shear wall holddown?

Typically long shear walls have an opening in them, if this is the case then you must reduce it's capacity, and it would be called a perforated shear wall.  Code does require that the end of each perforated wall to have a hold down.

RE: Can you ommit a shear wall holddown?

Remember that the anchor bolt are normally in shear in addition to the uplift.

RE: Can you ommit a shear wall holddown?

If it's a long wall and has an opening, just make it two sahear walls and put in more hold downs.  Forget the complicated analysis, use full values.  

If the h/t ratio comes into play (>2:1) to effectively reduce the allowable shear values, then maybe, depending on the hailing and holddown sizes.

I just try to KISS wherever possible. thumbsup2

Mike McCann
McCann Engineering

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources