Convert three phase available fault current to single phase
I used SKM to generate three phase available fault current.  Now I want to use something else to find single phase fault current and arc flash info.  How do I convert the three phase available fault into single and phase to phase available fault current.  I intend to use this info to plug in to the Duke Calculator.
RE: Convert three phase available fault current to single phase
SKM can calculate line-to-ground and line-line short circuit currents.
There is no universal conversion - it depends on the transformer connections and grounding methods (mostly) and a few other things.
Thanks, dpc.  No we haven't bought the unbalanced/single phase module.  So I was trying to investigate how to convert from three phase fault current at the bus to single /phase to phase.
All of the fault calculation options of SKM include all four fault types (3Φ, SLG, LL, LLG) whether or not you also have the single phase/unbalanced load flow module.
Wow, thanks.  As you can tell, I'm new to this SKM.  I was under the false impression that you had to buy the unbalanced module.  So what does it do for you if you buy that?
Single phase load flow; unbalanced load that aren't converted to balanced 3 phase when reported upstream; single phase panel schedules.
davidbeach,
You should be working on your WPRC presentation....
Dave
Who says I'm not?  It's still two days away and I only have two more minutes to shave out of it, down from being 10 minutes over.