re-tightening / overtightening connections
re-tightening / overtightening connections
(OP)
http: //www.cabl e.alcan.co m/NR/rdonl yres/5B486 C70-78C6-4 342-BE1A-6 3BDD3F9331 4/0/Applic ations.pdf
doc page 28/Adobe p. 30 - "Note that connections to NUAL conductors should not be tightened on a regular basis, as this may deteriorate the connection."
doc page 28/Adobe p. 30 - "Note that connections to NUAL conductors should not be tightened on a regular basis, as this may deteriorate the connection."






RE: re-tightening / overtightening connections
If you feel you must "maintain" then connection, the proper procedure is to loosen the connection and re-tighten to the specified torque.
RE: re-tightening / overtightening connections
RE: re-tightening / overtightening connections
"Bus Torque Specifications - Tighten all bus splice connections with a torque wrench and socket at intervals
established by your maintenance policy. See Chapter 9 for suggested maintenance. If a torque wrench is not available, tighten until the conical spring washer is flat."