NEC 2005 110.26(C) and Bus Ducts

NEC 2005 110.26(C) and Bus Ducts

NEC 2005 110.26(C) and Bus Ducts

(OP)
110.26(C) was revised in the 2005 NEC to pertain to equipment rated 1200A or more that contains overcurrent devices, switching devices or control devices. This deleted the exclusion of equipment less than 6'-0" in width.

Would a 1200A bus duct riser be defined as such equipment, subjected to the requirements of this section?

RE: NEC 2005 110.26(C) and Bus Ducts

The busduct would not be the type of equipment covered by this rule as it does not contain overcurrent devices, switching devices or control devices.  Also the 6' part of the rule is being restored for the 2008 code.
Don

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources