Hello. I posted this message on th
Hello.
I posted this message on the Bridge Engineering Forum.  But, did not get much respond to my last posting.  I hope someone maybe able to respond to my question here.
The reference I am trying to follow is "Bridge Substructure and Foundation Design" by Petros Xanthakos, example 4-5 p. 261.  Link: http://www.buildabout.com/forum.php?action=display&&item_id=51
Specifically, I do not understand how the factor distribution was derived in the frame analysis for the bridge interior and exterior columns.  Any help is much appreciated.
RE: Hello. I posted this message on th
vbridge,
There are few arithmatic/transposition errors in the distribution factors:
Assuming that the stiffness of the columns are indeed 0.058I, and the beams 0.083I, respectively, then the corrected DF values are:
DAD=0.083/(0.083+0.058)=0.59
DBE=0.058/(0.083+0.083+0.058)=0.26
I have not checked the moment distribution.
Is this want you wanted?
Ingenuity,
Thank you for your respond.
I don't know how to find the stiffness to the column and the beam.  How do I go about in finding the stiffness for the column and the beam? Also, I don't know how to arrive at the numbers above the beam, i.e. 9.7, -23.6, etc..
vbridge,
This is the MOMENT DISTRIBUTION technique which is a rapid, hand iterative method.
You calculate your fixed end moments (FEM's), your Stiffness factors, distribution factors, carry-over factors, then distribute the FEM etc.
It is a simple technique but a little cumbersome to explain on this firum. You will have to check out a STRUCTURAL ANALYSIS text - most basic texts will detail this very useful method.
HTH
Ingenuity,
I understand.  Thanks for your help.