Hi all!

Customer wants to test his motors.
He want Polarization Index, Hi-Pot and Surge Test.

I'm familiar with the 2 first test but what is a surge test?
He wants it to be done at 2,2 kV. What are the expected results ?

Thanks

RE: Tests on Electric Motor

It is a test where you apply a high-voltage surge to the windings and look at the response on a scope screen. It is an effective way to find hidden defects, like shorted turns etc in the windings. If all traces look the same, you usually don't have a problem.

Baker is (one of the existing) manufacturers.

Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...

RE: Tests on Electric Motor

unclebob,

This might help:  http://www.bakerinst.com/BakerWeb/PDF_Files/Benefits_of_Surge_and_Hipot_testing_of_Electric_Motors.pdf

Essentially, all three legs of a 3 phase motor should have identical induction character.  A surge test "rings" (pulses) each circuit path, and compares the decaying waveforms, superimposed.  They should have relatively high congruence.  If not, there is likely a turn-to-turn short that will cause failure later.

BK

RE: Tests on Electric Motor

The test is described in IEEE522.

Like the hi-pot, the surge test is potentially destructive, so you need a qualified person to perform the test and full agreement on the test voltages before you test it.  

=====================================
Eng-tips forums: The best place on the web for engineering discussions.

RE: Tests on Electric Motor

In addition to baker, PJ electronics makes surge testers. You might find more info on one of these test equipment manufacturer's sites.

=====================================
Eng-tips forums: The best place on the web for engineering discussions.

RE: Tests on Electric Motor

If your customer is asking for it then and specifying the test voltage, then there should be no issues. The problem i see with this test is that it is not qualitative - if a winding is old it will finish it off - the motor either passes and goes back into service, or fails and needs serious repair.

This is good if the machine is critical but if it is a non-critical machine that won't cause a process to stop if it fails (ie of you have redundancy) the I believe the test is not necessary.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources