Power XFMR 100MVA xfmr fault current
|
Power XFMR 100MVA xfmr fault currentPower XFMR 100MVA xfmr fault current(OP)
How do I determine the available fault current for a 100MVA xfmr base rating: 230KV delta/26KV wye with 7.5% impediance?
Red Flag SubmittedThank you for helping keep Eng-Tips Forums free from inappropriate posts. Reply To This ThreadPosting in the Eng-Tips forums is a member-only feature.Click Here to join Eng-Tips and talk with other members! |
ResourcesWhat is rapid injection molding? For engineers working with tight product design timelines, rapid injection molding can be a critical tool for prototyping and testing functional models. Download Now
The world has changed considerably since the 1980s, when CAD first started displacing drafting tables. Download Now
Prototyping has always been a critical part of product development. Download Now
As the cloud is increasingly adopted for product development, questions remain as to just how cloud software tools compare to on-premise solutions. Download Now
|
RE: Power XFMR 100MVA xfmr fault current
(I'm making an slightly skeptical assumption that this is not a homework problem.)
RE: Power XFMR 100MVA xfmr fault current
RE: Power XFMR 100MVA xfmr fault current
This result is the three-phase symmetrical fault current through the transformer for a fault on the low side. It does not included any contributions from motors on the low side, or other local sources.
RE: Power XFMR 100MVA xfmr fault current
Dpc, your calculation is correct, and that is the maximum amount of fault current the trandformer can produce. This fault current would be limited by the source feeding the primary side of the transformer.
Downstream of the Secondary side, the fault current would be reduced due to the impedance in the cable, thus the motors and other components in the circuit would not add to the fault current.
So, if trying to protect downstream devices, ensure the device you are using to clear the fault current (fuse, breaker) has an adequate interrupt rating.
Just wanted to add some info from my experience working at a fuse manufacturer.
Regards,
-Paul