Power XFMR 100MVA xfmr fault current
2

Power XFMR 100MVA xfmr fault current

Power XFMR 100MVA xfmr fault current

(OP)
How do I determine the available fault current for a 100MVA xfmr base rating: 230KV delta/26KV wye with 7.5% impediance?  

RE: Power XFMR 100MVA xfmr fault current

Take the transformer VA rating, divide it by the % impedance. then divide that by the voltage and 1.732.   Result is the maximum three-phase fault current through the transformer assuming an infinite source.  

(I'm making an slightly skeptical assumption that this is not a homework problem.)


RE: Power XFMR 100MVA xfmr fault current

(OP)
Thanks for the info.  And no, its not a homework problem.  I assume I would use the LV value?  hence that would provide the total available fault current?  I'm a T-line engineer trying to assist some overworked substation co-workers!

RE: Power XFMR 100MVA xfmr fault current

It works in either direction, just use the voltage for the side you are interested in.  Normally, for a step-down transformer, you'd be interested in the low side fault current that the transformer could produce.  

This result is the three-phase symmetrical fault current through the transformer for a fault on the low side.  It does not included any contributions from motors on the low side, or other local sources.    

RE: Power XFMR 100MVA xfmr fault current


Dpc, your calculation is correct, and that is the maximum amount of fault current the trandformer can produce. This fault current would be limited by the source feeding the primary side of the transformer.

Downstream of the Secondary side, the fault current would be reduced due to the impedance in the cable, thus the motors and other components in the circuit would not add to the fault current.

So, if trying to protect downstream devices, ensure the device you are using to clear the fault current (fuse, breaker) has an adequate interrupt rating.

Just wanted to add some info from my experience working at a fuse manufacturer.

Regards,

-Paul

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.