Mixing Types Cables in conduit or tray.
Mixing Types Cables in conduit or tray.
(OP)
Is it OK to mix 300v Cable and 600v Cable in the same condit or tray if all cables will be used at a voltage of 24v?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Mixing Types Cables in conduit or tray.
|
RE: Mixing Types Cables in conduit or tray.
392.6 (E) Multiconductor Cables Rated 600 Volts or Less.
"Multiconductor cables rated 600 volts or less shall be permitted to be installed in the same cable tray."
I think you're covered.
RE: Mixing Types Cables in conduit or tray.
RE: Mixing Types Cables in conduit or tray.
Thanks for the info. on the multiconductor cable and Tray. Does anyone else know where I can find the same infomation for conduit? I was told I can't mix 300v and 600v cables in the same conduit even though the voltage is 24v for all cables.
RE: Mixing Types Cables in conduit or tray.
Over 600 V it's a different story.