Pressurize a room

Pressurize a room

Pressurize a room

(OP)
If I know the leakage of my building; How do I know the amount of supply air (CFM) to reach a 0.1 in w.c. positive pressure? I have been reading some guidelines from ASHRAE journal and it refers to have a differential capability of 400 cfm to reach 0.01 in w.c. Is there any empirical way to estimate it? They also refers commom leakage through open doors (3'X 7')as 1050 CFM and 150 for closed doors.

RE: Pressurize a room

Why do you need .1"  that seems awefully high.  How did you arrive with that number ?

RE: Pressurize a room

(OP)
It was the same question I made; It comes from company's specs (electronic+hazardous room)

RE: Pressurize a room

I can't say that I'm an expert in this area but there is an equation found in ASHRAE that might apply to this situation.
DP = (Q/2610*A))^2.  Where dp is the diffential pressure (0.1" in this case), Q is the cfm, A is the area of leakage.
You can solve for Q to find the cfm, but you need to know what your Leakage area is.  The cfm required to maintain a certain differential pressure is dependent on construction type.

I know when designing negative pressure rooms in hospitals the cfm required to maintain a .05" pressure can range from 100 to 500 cfm difference between exhaust and supply depending on how tightly sealed the doors and ceilings are.
I also believe somewhere in ASHRAE they recommend no larger than about a .03" WC across a door so that it isn't too difficult to push open.

This probably doesn't completely answer your question, but maybe its a start.

RE: Pressurize a room

1050 cfm for open door (based on 50fpm velocity across the door opening)and 150cfm for closed door are good guidance values. That gives you some relief with the door bottom gap to be as high as 10mm. Oflate, the trend is not to use drop seals and this value can be useful if you plan to do so. If I use drop seals then I go for tighter OA control.

0.1"WC is quite common in pharma industry and you should really worry if the pressure is above 0.12"WC.

The thread403-196510: Airflow balance in hospital can be of help to you.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources