Medium Voltage Cable Testing

Medium Voltage Cable Testing

Medium Voltage Cable Testing

(OP)
I have heard differing opinions on whether or not to Hi-Pot test service aged medium voltage cable. What are the NETA standards in regard to this. These cables are approximately 3 years old at 13.2 kV.

RE: Medium Voltage Cable Testing

There has been a lot of discussion in previous threads on this topic.  I'd just emphasize that I would not do anything that was not recommended by the cable manufacturer for field testing of installed cable.

RE: Medium Voltage Cable Testing

Three year old cable is 'practially' brand new.

RE: Medium Voltage Cable Testing

whycliffrussel, three year old cable may have most of its expected life left, but for testing purposes it is used.  The differential between new and used is that it has been placed in service carrying AC load current.

RE: Medium Voltage Cable Testing

Once it's "pulled" in, it is definitely not new anymore.  

RE: Medium Voltage Cable Testing

NETA says to not DC hipot service aged cables >5 years old. A VLF ,Tan Delta, or PD test is recommended

RE: Medium Voltage Cable Testing

(OP)
whycliffrussel - While the cable is only three years old, the issue at hand is as follows: I will try to keep this as short as possible.
A customer of ours has 10 - 2 mW generators at 13.2 kV, one of these generators had a fault in the 15 kV cables leading to the PTs. These 3 - #14 15 kV cables were routed through the generator termination housing to the PTs through a 1/2" non metallic sealtite conduit. The fault occured in the middle of the sealtite which would lead one to believe there was some leakage that occurred. While this cable was non-shielded cable it is being replaced with shielded cable which is not being installed in conduit. It is however being routed away from other conductors in the enclosure. This faulting of the cables has prompted our customer to ask for testing of all of the existing cables on all of the generators.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources