Hi!

Simple question for you guys but one which I am not too sure of and need you help....

For example a control valve with 4-20mA input,  and a load resistance of 300ohm,  how do we use the 300 ohm load resistance information...

It must be  for selection of controllers but I am not too sure how to use this info.

Hope my question makes sense to you.

RE: Control Valve Input

Your loop has a 4-20mA current source which drives a defined current into an unknown resistance. The source has an upper limit on how much voltage it can deliver to drive the current around the loop, so at some point the loop resistance becomes too high for the current source to operate correctly with. Typically the limit is 20V or so, occasionally a bit higher. If your I/P converter has an effective resistance of 300Ω then at 20mA it will require at least 6V at the converter to drive it. From this result it is possible to size cables to ensure that total volt-drop around the loop from the source (PLC, DCS, etc) to the I/P converter is within the working range of the source.
 

----------------------------------
  
Sometimes I wake up Grumpy.
Other times I just let her sleep!

RE: Control Valve Input

The significance of the device was greater before digital controls when it was necessary to series devices in the 4-20 mA loop.  Typically you only have a transmitter and the I/O module in a loop.

With analog devices you might have needed a 4-20 mA alarm module for the high alarm, another alarm module, perhaps a summer if you needed to add two signals, include an analog meter at the transmitter and an intrinsic safety barrier.  Then the loop doesn't work.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources