Dear All.
I would like ask you some not correct Q.

On this week-end (Merfi law) we had several faults on the MV cables in the same factory and I'm looking for explanation in the forum.
I found many posts about HIPOT, PD tests of cables. I learn a lot and understand many things ( of course not all winky smile).
Many thanks to Benjamin Lanz for great explanation.

O.K., now my Q.: what is possible ( may be average ) price of  VLF HIPOT Tester in k$.  I would like recommend to several companies bay one unit.
Best Regards.
Slava

RE: VLF test of MV/HV cables

Baur test equipment in Austria produce a portable unit called a freda, it has an rms output of 23kv http://www2.baur.at/index.php?id=266&L=1.
Other manufacturers are HVinc in the states.
What is the system voltage?

RE: VLF test of MV/HV cables

(OP)
Hi.
Our MV is up to 36kV.
Fault cases on 22kV cables.
Thanks.
Slava.

RE: VLF test of MV/HV cables

Google VLF hopot, you will find several manufactures of these units. We use a hipotronics VLF with a tan daleta module, I think it is 50kV but I will have to check. About 10 grand if I recall.

RE: VLF test of MV/HV cables

(OP)
Dear Zogzog.
Thanks a lot.
I found several mnf, but I don't try bay it.
I only would like know what is a possible price level.
Test of cables it's not my area.
BTW, I hear about some ultrasound PD test, what is it?
Regards.
Slava

RE: VLF test of MV/HV cables

Slava,

You are welcome for the explanations.  The ultrasound technique is typically an on-line technique.  Ultrasound is only likely to detect PD activity when the probe is nearly in contact with the source.  This creates a very high potential for false negatives and positives.  Generally this technique is only useful for exposed cable components and can be expected to accurately detect < 3% of defects in cable systems

Benjamin Lanz
Vice Chair of IEEE 400
Sr. Application Engineer
IMCORP- Power Cable Reliability Consultants

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources