failing low-voltage dimmer

failing low-voltage dimmer

failing low-voltage dimmer

(OP)
hi all,
i have some 600VA low-voltage dimmers being used with a 120VAC/24VAC magnetic transformer.  this transformer is rated for 450 Watts.  the loads are 24V cove lights which have drawn as much as 350 Watts from the transformer.

back on the primary side, it is the dimmers that have been failing.  the measured amps from the dimmers is only around 3 Watts.

1) could the 350 Watts on the secondary side of the transformer equate into more than 600VA for the dimmer on the primary?

2) could in-rush current be a problem with a setup like this?

thanks for any help you can provide!

brother jb

RE: failing low-voltage dimmer

Transformers present an inductive load to dimmers.  They are often not designed to deal with the current offset this causes.  The result is blown dimmers.

Dimmers made for motors face the same problem.

Have you tried a "Motor Rated" dimmer in your setup yet?

Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com

RE: failing low-voltage dimmer

(OP)
I haven't tried a motor-rated dimmer.  the 600VA low-voltage dimmers are designed for magnetic, so i had hoped it would work.

can in-rush current be a problem with magnetic transformers?

brother jb

RE: failing low-voltage dimmer

What do you mean by 'low voltage' dimmers? What is the rated voltage of the dimmer? I assume 120V AC but best to check. Otherwise Keith is on the right lines: cheap dimmers tend to use a single trigger pulse to fire the triac or thyristors and with an inductive load the timing of the gate firing pulse can be such that the triac / thyristor does not latch on. Look for a burst-fired or hard fired type which either applies a series of firing pulses or a continuous gate current. Dimmers suitable for inductive duty usually advertise the fact somewhere because it is unusual and therefore a selling point.
 
 

----------------------------------
  
Sometimes I wake up Grumpy.
Other times I just let her sleep!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources