Grounding rebar in foundations

Grounding rebar in foundations

Grounding rebar in foundations

(OP)
We are installing a new pre-fab electrical building on a new foundation.  The engineering firm puts on the drawing to bond the rebar to the grounding system.  Does the rebar have to be bonded in any certain way?

RE: Grounding rebar in foundations

There are UL-approved connectors for this application.  The best is to use exothermic weld (Cadweld), but there are approved compression fittings as well.  Burndy makes a wide range of compression fittings for direct-buried grounding applications.  Cadweld and/or Burndy will be able to help you.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources