Modular Boilers Exhaust design

Modular Boilers Exhaust design

Modular Boilers Exhaust design

(OP)
Hi Guys,
I am looking assistance in finding exhaust header & stack sizes for 3 modular hot water boilers. Each boiler has 24" exhaust flange. I am planning to breach them in one common header & then connect to stack.
I have existing 2 stacks available each 16" big. How I find the common header size from 3 boilers exhausts & stack size. Can I use two stacks connected with one common header, this way size for required stack will be divided in two.
Appreciated for suggestions & any tech referneces.
Thanks

RE: Modular Boilers Exhaust design

rahim,

More information is required, what are exhaust gas flows and temperatures, lengths of ducting?

athomas236

RE: Modular Boilers Exhaust design

(OP)
Thanks for the response. I am sorry I don't have exhaust gas details as I am choosing the boilers directly from vendor catologue, capable of providing required duty. What I know is the exhaust size of each module (24").
The 3 boilers will be fitted in a boiler room (in basement) having 28'X19' space, while each module is 5.5'X4.5' in size. The two existing stacks (16" each) is located on opposite corner of room.
Again I will ask in general, can we connect two stacks with one common exhaust header (each on two ends), this will divide the exhaust gas into halves & stack size will be half.
Thanks agian
rahim

RE: Modular Boilers Exhaust design

Forced draft, induced draft, or natural draft boilers?

sorry, ya need to provide the data athomas236 stated or at least provide the boiler duty.

good luck!
-pmover

RE: Modular Boilers Exhaust design

(OP)
Hi,
Guys appreciated your help. Its natural draft & 3 modular boilers each of 49 H.P.
Regards

RE: Modular Boilers Exhaust design

rahim,

Here are some numbers for you to think about:

49HP @ 33472BTU/h for 1HP = 1.64million BTU/h=0.4806MW

With boiler efficiency of 75% and GCV of oil of 41MJ/kg,  fuel consumption is 0.4806/(41*0.75)=0.0156kg/s = 124lb/h

With 4% O2 in flue gas (dry volume basis) ratio of flue gas to fuel is 18.06, so flue gas flow is 2240lb/h.

With flue gas temperature of 300C, gas constant of 286.7J/kg K and limiting gas velocity of 15m/s, the required duct diameter is 8 inches.

Of course all these numbers are all rough estimates and are made without any knowledge of your actual plant, but at least you have numbers.

Regards,

athomas236

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources