Sprinklers in MCC Room
3

Sprinklers in MCC Room

Sprinklers in MCC Room

(OP)
In the case of MCC Rooms, is there an exception to a typical bujilding department rule requiring fire sprinklers if an area exceeds, say, 5000 square feet?
If the MCC room has firewalls, is it exempt from the sprinkler requirement?

RE: Sprinklers in MCC Room

MCC room size is 5000 Sq.ft .Cost of MCC panels /Saving time /Production is most important.if you can provide sprinkler in MCC room is best safety practice.You can prevent the fire furthera and will save lot.

RE: Sprinklers in MCC Room

Go for a pre-action sprinkler system and then dump power before water arrives at the electrical equipment.

RE: Sprinklers in MCC Room

Search the archives, there has been at least one previous thread on this exact subject.

RE: Sprinklers in MCC Room

The fire marshall will make you cover the room with sprinklers no matter what.  We had a Generator Control and synchronizing switchgear room in a central utility plant with 12kV gear in it and they still insisted that it be fully covered with sprinklers- even though the gear was only NEMA I and the switchgear fed the emergency loads for an entire hospital-I doubt the MCC will be much different, but you should check with your AHJ.

I don't get the logic, but that's what I've seen happen.

Good Luck.

RE: Sprinklers in MCC Room

Well the logic is.. When the temperature is so high that the sprinklers are going off the electrical is about to be toasted anyway.

Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources