115 kV cap bank in a ring bus

115 kV cap bank in a ring bus

115 kV cap bank in a ring bus

(OP)
Have you ever seen capacitor banks as one of the terminals in a 115 kV ring bus? If so, what kind of separate isolation or switching device besides the two breakers did it have?

Thanks

RE: 115 kV cap bank in a ring bus

I worked for a utility for few years and saw a number of 138kV cap banks connected in a ring. This utility always used a controlled switching device (Synchronous, Pre-Insertion Resistor, etc.) between the cap bank and line position. The utility also required that the line breakers be capable of interrupting the capacitive current of the bank. This would provide an interrupting device if the controlled switching device failed.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources