embeded generator on the utility feeder
2

embeded generator on the utility feeder

embeded generator on the utility feeder

(OP)
I ran some models with embeded generation on utility feeder and I found that SC level seen by the TS relay protection remained constant.
However I came across some papers that say relay will see SC current decrease with new generation connected downstream on the feeder. This doesn't make sense to me.

Any comments?
Should I expect TS relay to see more or less curent for baulted 3phase fault with generation on?

RE: embeded generator on the utility feeder

TS relay?  Please define your terms.

RE: embeded generator on the utility feeder

More sources generally means more fault current.

What is an "embedded" generator?

RE: embeded generator on the utility feeder

(OP)
Thanks guys.
To clarify:
Embeded generator is generator that normally work in parallel with the grid.

TS relay is Transformer Station relay, this is first upstream protection of the feeder with embeded generator

RE: embeded generator on the utility feeder

If this is relay is in between the normal grid power source and the local generator, it may never see the combined fault current from both sources.  If the fault is downstream, it will see the normal source contribution.  If it is upstream, it sees only the contribution from the local generator, and this will indeed likely be very small.

For coordination purposes, you will need to look at both fault conditions.

RE: embeded generator on the utility feeder

2
The local generation and the transformer station source are basically in parallel.

CODE

TS----Z1------+------Z3-------X
     ---->    |     ---->
      ITS     |      IF
              |   ^
              Z2  | IG
              |   |
              |
              G
Current in the fault X comes from TS and from G.  Current from G will increase voltage drop in Z3 (compared to drop without G) and reduce the current coming from TS.

RE: embeded generator on the utility feeder

Jghrist, I'm not understand, why current from G reduce current from TS.
Could you please explain.
Regards.
Slava

RE: embeded generator on the utility feeder

(OP)
Jghrist:
thanks a lot.
So it is not that impedance will be apparent for the relay in the TS, but also overcurrent protection will be measuring apparent current which is less then the current that the same relay measures w/o the generation. Great !

RE: embeded generator on the utility feeder

(OP)
Jghrist - star for you!

RE: embeded generator on the utility feeder

slavag,

Use the diagram in my previous post and take an oversimplified example.  Put a 150V source at both G and TS, tying the negative side back to the fault location X.  Make all impedances 10 ohms.  Without G, the current ITS = IF = 150/(10+10) = 7.5A.  With G, the G and TS sources will be in parallel, IF = 150/(10+10/2) = 10A, half (5A) will come from G and half from TS.

RE: embeded generator on the utility feeder

Jghrist.
Thanks a lot.
Haha, with time we forgot also ohms law and parallel connection of resistors smile.
Regards.
Slava

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources