Motor Winding Trip Temperature

Motor Winding Trip Temperature

Motor Winding Trip Temperature

(OP)
What is the max permissible temperature ( trip temp ) an F motor insulation can withstand for a short time before motor trip ?
I've read in Sprecher & Schuh documentation that motor F insulation can withstand a short-time temperature of approximately 250°C before motor trip.
F insulation continuous operating temp = 155°C - 10°C hot spot allowance = 145°C.
The settings for the ABB REF542plus motor protection relays includes the motor heating time-constant which can be determined by :-

Heating Time-Constant ( Tor ) = Motor Permissible Locked Rotor time from Cold / ( nat log ( motor LRC^2 / ( motor LRC^2 - k^2 ))).
Where LRC = motor Locked Rotor Current ( starting Current )
Where k = overload factor = (( Trip Temp - Amb Temp ) / ( ( Rated Temp - Amb Temp ) )^0.5





  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources