Motor Max Fuse Size Tables?
Just some info Req:
Does any have or know where I can get a table that shows the max fuse sizes (Time Delay) that can be used by code (CSA if possible) for a particular motor (@ a specific Voltage based on its FLA)
I could make one, for example at 600V (575V motors)
Motor FLA Max Time Delay Fuse
10HP 11A 15A
50HP 52A 80A
10HP 11A 15A
50HP 52A 80A
RE: Motor Max Fuse Size Tables?
I'd contact Bussman and Shawmut, I'm sure they will be happy to help if it might sell a few fuses.
Thanks guys, slide rule is an awesome idea. I'll have to ask for one!
I started making an excel spread sheet. So far it is just for single motor branches: HP, FLA, TD Fuse and Cable size... man what a time saver then grabing the calculator and flipping through the tables.
Just a note: It is Table A24, of the old Consulting Application Catalog (pg A-58, Jan 1999)
htt
And Table 1.5-2 of the recent catalog (pg 1.5-7 June 2006)
http://www
In the 1998 edition of the CEC it was moved to table D12.
(Appendix D Tabulated General Information)
In the 2006 edition of the CEC it is Table D16.
See also Table 29 in either edition of the CEC for percentages.
Please note: The NEC refers motor horsepower to a table which gives the motor current to be used based on motor horsepower rather than nameplate ratings.
The CEC uses nameplate current.
respectfully