Anybody ever hear of a "Modified Header System"? I ran across it in an HVAC handbook (by Arthur Bell). It warns not to use it as it causes operational problems. Says it does not work. What does it look like? Just curious.





RE: HYDRONIC PIPING
RE: HYDRONIC PIPING
RE: HYDRONIC PIPING
I am not aware of any operational problems and there should not be any.
RE: HYDRONIC PIPING
If a unitized system has dedicated pumps for each chiller/boiler, and a manifolded system has all pumps connected to a manifold that in turn feeds multiple chillers/boilers, the "modified manifold" would be where some boilers/chillers have a dedicated pump and some don't. You can see the problems if one pump has to be used for one chiller, but multiple (manifolded) pumps can serve another chiller. There are redundancy issues for one thing. If all chillers/boilers are not the same capacity, you need to use a unitized system or some hybrid like a "modified manifold" system but have the appropriate controls.