Fire pump room requirements
4
Does NFPA 20 require that the pump room be dedicated exclusively to the fire pump equipment? Due to space limitations, we wanted to have a pump room that would contain the hot water and chilled water pumps along with the fire pump. The room is 2 hour rated and will be sprinkled.
Chaz
RE: Fire pump room requirements
where are you sticking this??? high rise, warehouse, one story office building????????
NFPA 20, 2007 A5.12.1.1.1 As long as the equipment does not pose a fire hazard, i.e. a boiler, it is OK.