AUTORECLOSER TRIP

AUTORECLOSER TRIP

AUTORECLOSER TRIP

(OP)
We recently replaced an 11kV aurocloser with a smrc type of autorecloser having an R6 controller. All the pre-commissioning tests were ok but when we put it into service it tripped on an earth-fault.

I decided to disable the ground fault and closed the bypass swith. There were currents of 100A, 0 & 30A on the A, B & C phases respectvely.

The former switchgear failed after one of the leads to its bushing terminals snapped burning the porcelain insulators(the controller had been accidentally switched off by an operator and it was apparently left off. Before the breaker behind operated, serious overheating of the porcelain insulators (especially on the B phase) on which the taplin isolators are mounted.

Could there be a problem with the CT wiring or could overheating have affected the insulators, reducing their creepage distances and thus causing some leakage to the steel channel on which they are mounted?

RE: AUTORECLOSER TRIP

Gee, 0A on phase B? Something seems really strange. Even 100A and 30A on A and C seems pretty strange. Those currents, if real, imply a lot of ground current, and if they are in the CT leads, then the recloser is sure going to think there is a ground fault. I do not know if bushings can open internally without it being obvious, but sounds like there is an open or short somewhere.  

RE: AUTORECLOSER TRIP

Maybe you have an open in the B phase CT, causing both the zero current measurement and arcing and heating from the high open-circuit voltage.

RE: AUTORECLOSER TRIP

(OP)
The auto-recolser, if put into service without the bypass switch, trips on very high currents (500Amps on B and neutral.). I hane been suspecting that the porcelain insulator onwhich the taplin isolator rests(B-pahse) has some leakage and as such the current flowing to the B-Phase autorecloser terminal is diverted to ground.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources