Extended coverage heads and window sills.

Extended coverage heads and window sills.

Extended coverage heads and window sills.

(OP)
I am dealing with a building designed per NFPA #13R (2002)using an extended coverage sprinkler having a maximum throw of 24'-0".

Distance from wall to wall is 23'-11".  

Each room has a single window where the sill is begins 3' above the floor with the window pane recessed creating a sill depth of of 6". Total distance between wall and window pane is 24'-5".

I've never worried about simple window sills before in any application.   

From Appendix.

A.6.7.1.5.3 Fire testing has indicated the need to wet walls in the area protected by residential sprinklers at a level closer to the ceiling than that accomplished by standard sprinkler distribution. Where beams, light fixtures, sloped ceilings, and other obstructions occur, additional residential sprinklers could be necessary to achieve proper response and distribution, and a greater water supply could be necessary.

Small areas created by architectural features such as planter box windows, bay windows, and similar features can be evaluated as follows:

(1) Where no additional floor area is created by the architectural feature, no additional sprinkler protection is required.
(2) Where additional floor area is created by an architectural feature, no additional sprinkler protection is required, provided all of the following conditions are met:
(a) The floor area does not exceed 18 ft2 (1.7 m2).
(b) The floor area is not greater than 2 ft (0.65 m) in depth at the deepest point of the architectural feature to the plane of the primary wall where measured along the finished floor.
(c) The floor is not greater than 9 ft (2.9 m) in length where measured along the plane of the primary wall.

[b]Measurement from the deepest point of the architectural feature to the sprinkler should not exceed the maximum listed spacing of the sprinkler. The hydraulic design is not required to consider the area created by the architectural feature.[b]

=================

I guess a window sill could be regarded as an architectural feature but I've always thought of this section to mean unusually deep architectural features one might expect in a bay window or extra deep pocket.

I've got lots and lots of water pressure; does anyone know of a quick response sprinkler with listed coverage greater then 24'?

RE: Extended coverage heads and window sills.

(OP)
To answer my own question.

http://www.vikinggroupinc.com/databook/sprinklers/standard/qr/excov/102905.pdf

Quick response with a throw up to 26'.  I've got 140 psi to work with at the sprinkler so the worst that would happen is I would have to change heads out.  Not good but not a rip roaring disaster.

8.7.3.3.2  The distance from the wall to the sprinkler shall be measured perpendicular to the wall.

It says wall and not "window pane" or "surface".


Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources