Multiple Battery Charger Demand
Multiple Battery Charger Demand
(OP)
Anyone know what sort of demand factor could be applied to the AC input load of multiple battery chargers for golf carts? This involves over 50 carts. I'm assuming the chargers are integral with the carts but not being a golfer I don't know if this is true. Not that it would matter.






RE: Multiple Battery Charger Demand
The demand factor will be 100% UNLESS you have specific information otherwise.
Bear in mind the consequences of a "loss of revenue event" due to not enough carts being ready when needed due to an inappropriate demand factor.