Oxygen concentrations after inerting
I have a question with respect to residual oxygen concentration in a process unit, vessel etc after inerting.
The usual limit of oxygen (in nitrogen) I have usd in refineries are 0.5 or 1.0 vol% after an inerting step. The the inerting is regarded to be complete and accepted. However looking at figures such as LOC combined with LEL/HEL this figures is about 11-12 vol% oxygen.
In my past I have been accustomed to use the 1.o vol% limit without giving it much consideration. however I cannot find a god explanation why such a low number should be used. Pratically I can buy into using a margin from e.g. LOC to cover for uncertanities in sampling/analyses and that all part of a unit/system that has been subject for the inerting havent mixed ideally. Naturally if hydrogen can be present I an see a reason for a lower limit, but in the case there is no hydrogen present, should the limit be this low?
The 1.0 vol % seems to be an industry practice. Is there anything I forget, overlook here.
Would be very much interested to hear others view on this subject.
RE: Oxygen concentrations after inerting
You may find some answers by visiting thread798-33615: How to Calculate Flammability of gas mixture and thread135-116595: Flammability limits in oxygen and the links therein.
Some degradation mechanisms due to O2 are difficult to predict before hand and the designers assumed an O2 free environment. That could also be a reason why the industry standard is to get the O2 level down as far as possible before introducing process fluids.
Some examples of damage due to "higher" levels of O2, I can think of: degredation of MDEA - corrosive products will manifest themselves after months; pitting if there are Cl ions.